mspohr
Well-Known Member
One minor point... the amperage won't change with longer cords... you put 20amps in and you get 20 amps out the other end.A proper wire ampacity table will have amp ratings also based on insulation heat specifications. So it isn't just the wire gauge, but also insulation heat capabilities. Also bear in mind that NEC tables are meant for in building wiring, not extension cords. And then you have resistance per length of wire. So you could be drawing 16A from an extension cord, but at the other end of a 100' long cord, the breaker could be seeing a 20A draw. Fwiw, in building romex is normally 14 gauge for 15A circuits, and 12 gauge for 20A circuits.
OTOH, you do get a voltage drop with longer cords. You could put in 120 volts and only get out 100 volts if you have a high current draw and a skinny wire.
Here's a good guide to extension cords:
Buying Guide: Extension Cordsat The Home Depot
Tesla charging would be considered "Extra Heavy Duty".
Tesla limits charging from 120volts to 12 amps which is 80% of the 15 amp capacity of these sockets required for continuous duty. For this, a short 14 gauge extension cord is minimum... better to have a 12 gauge cord.