Just recently got my system installed here in San Jose (city), Tesla scheduling final inspection. Interconnect was filed in time for NEM2.0….
10.8kW PV, 4x ESS (54kW).
3x EV’s (Model Y).
PGE EV2A rate plan.
Currently have 200A service. 200A main panel (but backed up loads limited to 100A by 100A max branch breaker on the main panel).
Tesla removed the extra load center, and was able to tie all 4 powerwalls directly into the GW2, with the optional sub panel board (that was a nice surprise).
I was also able to convince Tesla to preemptively install #2/0 (instead of AWG #3) for both the main to GW2 and also GW2 to Backed Up load center / distribution panel (which has a 225A bus bar). In theory this should make for an easy upgrade to a new main panel that is 200A as well as 200A rated on a max branch breakers…
If I do that upgrade it would allow me to change the backed up load center to 200A breakers instead of current 100A…and move my two EVSE loads (48A continuous, 60A breaker / OCPD) from the non-backed up main over to the backed up load center.
Question is…is that a good thing, bad thing or moot / don’t care?
I understand that even one EV needing like 60% of charge (Tesla Y’s are like 82kW, right?) will consume my 4x powerwalls…much less 3x EV’s.
And also, in an outage, I’ll likely want to conserve my powerwalls and not charge EV’s (but Tesla kinda manages that with the setting where you can limit EV charging during an outage).
But for Time Based Control to have the most data to make the best monetary optimizations…isn’t it better to have all loads backed up?
Also, that way I can see the EV consumption on the app. If they weren’t backed up I could not.
10.8kW PV, 4x ESS (54kW).
3x EV’s (Model Y).
PGE EV2A rate plan.
Currently have 200A service. 200A main panel (but backed up loads limited to 100A by 100A max branch breaker on the main panel).
Tesla removed the extra load center, and was able to tie all 4 powerwalls directly into the GW2, with the optional sub panel board (that was a nice surprise).
I was also able to convince Tesla to preemptively install #2/0 (instead of AWG #3) for both the main to GW2 and also GW2 to Backed Up load center / distribution panel (which has a 225A bus bar). In theory this should make for an easy upgrade to a new main panel that is 200A as well as 200A rated on a max branch breakers…
If I do that upgrade it would allow me to change the backed up load center to 200A breakers instead of current 100A…and move my two EVSE loads (48A continuous, 60A breaker / OCPD) from the non-backed up main over to the backed up load center.
Question is…is that a good thing, bad thing or moot / don’t care?
I understand that even one EV needing like 60% of charge (Tesla Y’s are like 82kW, right?) will consume my 4x powerwalls…much less 3x EV’s.
And also, in an outage, I’ll likely want to conserve my powerwalls and not charge EV’s (but Tesla kinda manages that with the setting where you can limit EV charging during an outage).
But for Time Based Control to have the most data to make the best monetary optimizations…isn’t it better to have all loads backed up?
Also, that way I can see the EV consumption on the app. If they weren’t backed up I could not.