Ummmm.... Use the same adapter we've been using all along?
Water-fun-guy says he doesn't want to use adaptors.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Ummmm.... Use the same adapter we've been using all along?
In theory you could do that, but it wouldn't be to code. (Since Tesla calls out that each Wall Connector needs its own breaker.Is this not possible on one breaker???
Yep, a small sub-panel would do it.Sounds crazy but maybe a sub panel in the garage with two 40 amp breakers and set the wall connector to never pull more than 32amps? Thanks
Yes, that's true.Hi all, a bit confused by Tesla using the term ‘Power Sharing’. Gave me the impression I could connect a second Tesla Gen 3 Wall Connector to the existing 40amp circuit breaker and tell them they only had 32amps to share.
No, not true.It seems they actually want each Wall Connector to have its own 40amp(or 50 or 60) breaker and be told how much total amps they can pull from the home panel.
I think this does work, but I am not entirely sure if the J1772 version and Tesla plug version can directly be configured to share together. I think they can, but I'm not sure.Would like to have my Model S and my wife’s Bolt both connected to a standard Tesla Wall Connector and a Tesla J1772 Wall Connector and have them figure out how to split up the available amps.
Right--that's how the sharing works. You can run one single 40A circuit to the garage to a subpanel. And then you could put up to 6 wall connectors on it, and set them each for 40A circuits if you want, but also set in the configuration that the total of all units together can't exceed the amount of the parent 40A circuit.Sounds crazy but maybe a sub panel in the garage with two 40 amp breakers and set the wall connector to never pull more than 32amps? Thanks
OK, sorry, trying not to be dense, looks like you are saying ‘Yes’ that it is OK to hook both wall connectors to one 40amp breaker in the main panel AND also say ‘right’ that it can have a sub panel in the garage running off the one 40amp with two 40amp breakers that the connectors share to pull no more than 40 amp(32 actually). Are you saying both options are acceptable? My electrician is looking at the manual and saying they both need to be on their own dedicated circuit breaker.Yes, that's true.
No, not true.
I think this does work, but I am not entirely sure if the J1772 version and Tesla plug version can directly be configured to share together. I think they can, but I'm not sure.
Right--that's how the sharing works. You can run one single 40A circuit to the garage to a subpanel. And then you could put up to 6 wall connectors on it, and set them each for 40A circuits if you want, but also set in the configuration that the total of all units together can't exceed the amount of the parent 40A circuit.
Per Tesla they have to be on seperate breakers. They will count as one load though for load calcs. Two options that come to mind are some tandem breakers (to make room for a second double pole breaker) or a sub panel.Hi all, a bit confused by Tesla using the term ‘Power Sharing’. Gave me the impression I could connect a second Tesla Gen 3 Wall Connector to the existing 40amp circuit breaker and tell them they only had 32amps to share. It seems they actually want each Wall Connector to have its own 40amp(or 50 or 60) breaker and be told how much total amps they can pull from the home panel. Basically I have an older home and I don’t have room for another breaker. Would like to have my Model S and my wife’s Bolt both connected to a standard Tesla Wall Connector and a Tesla J1772 Wall Connector and have them figure out how to split up the available amps. Is this not possible on one breaker??? Sounds crazy but maybe a sub panel in the garage with two 40 amp breakers and set the wall connector to never pull more than 32amps? Thanks
They each need their own breaker, but they don't each need a dedicated circuit in the main panel. You could attach a small load center (with two 40a breakers) to the existing circuit near your current wall connector, then run wires from there to both of them. So they are both attached to the same 40a breaker in your main panel, but each also have their own breaker in the load center.OK, sorry, trying not to be dense, looks like you are saying ‘Yes’ that it is OK to hook both wall connectors to one 40amp breaker in the main panel AND also say ‘right’ that it can have a sub panel in the garage running off the one 40amp with two 40amp breakers that the connectors share to pull no more than 40 amp(32 actually). Are you saying both options are acceptable? My electrician is looking at the manual and saying they both need to be on their own dedicated circuit breaker.
Oh, I am sorry. I made a mistake in reading what you said. You did say "the existing circuit breaker". You can't just physically branch the power wires with like Y splitting from only one breaker.OK, sorry, trying not to be dense, looks like you are saying ‘Yes’ that it is OK to hook both wall connectors to one 40amp breaker in the main panel
Yes, that is the method it has to use, where it uses a subpanel to divide it out, with a breaker for each.also say ‘right’ that it can have a sub panel in the garage running off the one 40amp with two 40amp breakers that the connectors share to pull no more than 40 amp(32 actually). Are you saying both options are acceptable?
People get a little unclear on the meaning of that word "dedicated". It doesn't have to be completely separate runs all the way back to the main panel. The individual wall connectors join into a subpanel that is basically sharing the incoming feeder line into that subpanel.My electrician is looking at the manual and saying they both need to be on their own dedicated circuit breaker.