I installed a TT-30 socket in my garage - just like any standard 120v outlet - but hooked up to a 30amp breaker with 10 gauge wire.
I purchased a TT-30 plug and a 10-30 socket and one foot of 3-10 wire.
The TT-30 has 3 wires, one hot, one neutral, one ground.
The 10-30 wants 3, two hots, and one ground.
I wired the TT-30 hot to one of the 10-30 hots, I wired the TT-30 neutral to the other 10-30 hot.
I connect the 10-30 pigtail into the charger ( An RFMC ).
I plug my 10-30 pigtail into the 10-30 socket on the connector, and the other end: TT-30 plug into the TT-30 socket.
The charger signals the 24amp pilot signal to the car, and it happily charges at 120volts.
I ask Tesla drivers to respond to my question:
Can the driver adjust the amount of current the EV will draw from a 14-50?
If the driver were plugging into a RV park's 14-50, it would be connected to a 50Amp breaker, so the most the EV should draw is 40Amps.
If the driver were to plug into a 14-50 that was on a 40A breaker, could the EV be set to only draw 32A?
Reason for asking:
I have been volunteered to do some upgrades on a charging set up the eaasv.org uses at their annual EVent at Palo Alto, CA HS.
The EAA member that built this was a EE, and has since past away. I am trying to retrofit it so as to give it more life/use at EVents. He built it in the 1990's when even the GM EV1 was new. So most of the time, only level 1 drawing conversion EVs would plug in. Hence it has gobs of 5-20 (regular 120VAC 20A) outlets. I am going to remove eight of the 5-20 outlets and install two 14-50 outlets connected to a 40A breaker.
Public EVSE is connected to a 40Amp breaker, providing up to 32A (by electrician code).
Please let me know if a Tesla EV uses one of their 14-50 adapter cables, what it Amperage
circuit it requires, and if it can work off a 40A breaker'd circuit or does it require a 50A breaker'd circuit.
Thank you,
-Bruce
Yes, Tesla can charge at reduced current off of NEMA14-50. It is configurable in the car to whatever rate you want (basically in 8A steps with some exceptions.)
I charged the LEAFat the PA EAA Rally and it only worked from the "pedestal" on the left (away from the parking lot). The one on the right caused some sort of ground fault and my EVSE kept shutting off.
So, if you are working on that stuff, try to make sure Neutral and grounding are all done right so that GFCI and other safety checks don't kick in.
There were more LEAFs than any other kind of EV at that Rally now, and that trend will likely continue next year.
Many LEAF owners have portable EVSEs modified to charge from L60-20 240V@16A.
Providing some L16-20 sockets might neaten up the cabling a bit...
(At the Rally I used a 14-50 to L6-20 adapter...)
Last edited by TEG; 10-14-2011 at 04:41 PM.
Bruce,
the quick answer is yes.
The Roadster can automatically and manually adjust current. I understand that US breaker ratings are in 10A steps (20,30,40,50) and that continuous load should be at 80% max breaker rating.
The Roadster adheres by offering following values for manual selection 16A, 24A, 32A, 40A. Minimum is 12A and it goes up to 70A.
Most Roadster enjoy the convenience of automatic selection, provided by extra circuitry in the adapter cables.
For example, the NEMA 14-50 adapter cable signals 40A max to the car charger, and the NEMA 10-30 signals 24A.
There is no adapter for a 40A line that signals 32A, though. Every Roadster owner would have to set 32A by hand.
I am fairly sure your efforts will be greatly appreciated by any visitors. They will happily charge at 32A. Chances are, someone will blow the 40A breaker by charging right away with the automatic value of 40amps. To get on the safe side, the two NEMA 14-50 outlets should have 50A breakers, or you should put up BIG signs saying 32A max charge current.
Last edited by VolkerP; 10-14-2011 at 04:56 PM.
Thank you all for your answers. So, I can use a 40A breaker on the two 14-50 outlets I will be adding. I will be clearly labeling each outlet as to what power they offer. The large panel has a 125A service disconnect breaker (the panel's main breaker).
If for example, I had all four of the 14-50 outlets I am planning for, being used by: two Tesla's and two Leaf EVs, all should be OK as the Leaf EV only has a half-powered (3kW) on-board charger. It would be like using the same power as if I there were only three Tesla's drawing 6kW each (well within the spec of the 125A panel with all other breakers off).
Because there was so many post-2010 Production EVs at the eaasv.org EVent is why I am making the effort to make the large panel more usable. It was originally built for the needs of the late 1990's. Clearly there are far fewer level1 needs than level2, and they will be for 6kW level2 power.
That was made quite clear, as you said, as there were many Tesla Roadsters at the EVent. First thing in the morning I saw them in come in one right after the other. Wow, that was about $1M worth of EVs right there! Each of the public I talked to that day I made sure they knew that the Tesla drivers were very generous in coming and letting the public put their dirty feet in their sweet ride. My thanks to you all.
I was aware at the end of the EVent that the large panel did have a grounding issue. A Leaf EV that was using one of their modified level1+ rev2 EVSE (a level 1 EVSE changed to provide either level1 or a 3kW level2), also had a fault as well. The Chapter's electrician said the panel was not hooked up right (he did the work so he would know). I am hoping that with due diligence to remind the electrician of this will ensure a proper hookup of the HS' 208VAC power, thus we will not have that issue again.
The chapter has two panels, a large 125A panel (the one I am working one), and small panel. It was that smaller panel that TEG used to get a charge. Some history: both of those panels had charged the original first run older-Production EVs in the late 1990's (EV1, RAV4-EV, Honda+, Think, etc.) when that Chapter's EVent was held at Stanford University.
By my adding of two more 14-50 outlets to the large panel, will let it have a longer use/life.
Thanks again,
-Bruce