Not anymore. Manual requires #2.
#3 is fine:
"Local regulations" would be the municipal, county, or state's adoption of the NEC.
I have confirmed with Tesla that they do not intend to demand #2 conductors.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Not anymore. Manual requires #2.
@FlasherZ, have you really posted 6,969 times? I usually can't make heads or tails of your posts, but that'll surely go down as a TMC record! Congrats.#3 is fine:
"Local regulations" would be the municipal, county, or state's adoption of the NEC.
I have confirmed with Tesla that they do not intend to demand #2 conductors.
@FlasherZ, have you really posted 6,969 times? I usually can't make heads or tails of your posts, but that'll surely go down as a TMC record! Congrats.
Not anymore. Manual requires #2.
For 80A operation, use 2AWG 194°F (90°C) rated copper wire or follow local regulations.
#3 is fine:
View attachment 180090
"Local regulations" would be the municipal, county, or state's adoption of the NEC.
I have confirmed with Tesla that they do not intend to demand #2 conductors.
Yes I keep forgetting about the "or" in that statement. But clearly someone put #2 in the manual for a reason. It doesn't seem proper to go under the recommendation in the manual because it meets local code, which is really wording for meeting the minimum passing grade.
Building codes, electrical or otherwise, are minimum passing grade.they don't consider it a "minimum passing grade" - it fully complies with Code and best practices, if available.
Building codes are actually incredibly conservative, and continue to get more so with time. They have to take into account wide variability in actual manufacturing and installation of materials, so they're only "barely passing" for that part of the variables that everything has issues. On average, there's still a wide margin of error.Building codes, electrical or otherwise, are minimum passing grade.
Building codes are actually incredibly conservative, and continue to get more so with time. They have to take into account wide variability in actual manufacturing and installation of materials, so they're only "barely passing" for that part of the variables that everything has issues. On average, there's still a wide margin of error.
Thanks for the review! I am also going to get a permit inspection done by next week. This is good to know, so perhaps I should set the HPWC to do 70Amp or less to be on the safe side. Please note my X wont be pulling any more than 48A, so does that alleviate concerns ? I reason I got the HPWC is because it gives me a better, hardwired, relatively more resilient option than UMC+NEMA14-50. Plus the added benefit of pairing it up with another HPWC on the same circuit for the Model 3 next year. I dont plan to have dual chargers on that either, happy with 48A,#4 copper NM cable (Romex) is only good to 70A (56A Tesla charging current) because you're required to use the 60 degree column in 310.15. It's an illegal install to use it to feed an HPWC set to 80A charging. It's ok to feed your subpanel with that provided it's protected by a maximum breaker size of 70A in the main panel.
#4 is permitted to handle 100A only when it feeds an entire dwelling unit. Under all other circumstances it's good to 70A (NM/Romex, or SER when put through thermal insulation) or 85A (wire in conduit @ 75 deg termination temp). Remember that circuit ratings need to be 125% of the charging current because charging is a continuous load.
I'm not sure about that other signaling conductor, it's likely just part of the cable assembly Tesla uses and is left unused.
Heck even 4AWG THHN at 90° is only good to 95A. The electricians probably just figured "hey, we feed 100A subpanels with this all the time, so we're good, right?" It's frustrating how many electricians are unaware of different rules for different uses. For example, I have a coworker who is building a house, and has a reservation for a Model 3 (and has eyes on an X if finances would allow). I'm trying to explain to him how best to pre-wire for two charging circuits. Given that with two 14-50s totaling 100A you may as well use the new wall connector and deliver 100A to each and let them share. So he asks his [cookie cutter] builder salesman, who comes back with "k, two 220v lines to the garage, with a 14-50, 40A wiring, on a 30A breaker. Got it!" The only way I can fathom the guy ended up there is prior experiences with RVs that connect to a 14-50, but never draw nearly that much current, and certainly not continuously.#4 copper NM cable (Romex) is only good to 70A (52A Tesla charging current) because you're required to use the 60 degree column in 310.15. It's an illegal install to use it to feed an HPWC set to 80A charging. It's ok to feed your subpanel with that provided it's protected by a maximum breaker size of 70A in the main panel.
I'm not sure about that other signaling conductor, it's likely just part of the cable assembly Tesla uses and is left unused.
You should set your wall connector to 70A/56A continuous, and replace the breaker to the wall connector and to the subpanel with 70A instead of 100A breakers. NEC rules are typically to prevent problems not just with what you currently have connected, but what anyone coming to the location might connect. I.e. if you have a friend come to visit with an 80A dual charger S, and he happens to plug in, it will still be safe.Thanks for the review! I am also going to get a permit inspection done by next week. This is good to know, so perhaps I should set the HPWC to do 70Amp or less to be on the safe side. Please note my X wont be pulling any more than 48A, so does that alleviate concerns ? I reason I got the HPWC is because it gives me a better, hardwired, relatively more resilient option than UMC+NEMA14-50. Plus the added benefit of pairing it up with another HPWC on the same circuit for the Model 3 next year. I dont plan to have dual chargers on that either, happy with 48A,
Thanks, I understand and agree, it occurred to me while my car(s) may not be a problem, a visiting car may pull more the rated/supported amperage leading to issues. I have also heard that breakers dont trip at the rated amperage but after a tad more tolerance (viz. a 50 Amp breaker would trip at 60Amp) - this sounded nonsensical to me.. curious if that's the case?You should set your wall connector to 70A/56A continuous, and replace the breaker to the wall connector and to the subpanel with 70A instead of 100A breakers. NEC rules are typically to prevent problems not just with what you currently have connected, but what anyone coming to the location might connect. I.e. if you have a friend come to visit with an 80A dual charger S, and he happens to plug in, it will still be safe.
Thanks for the review! I am also going to get a permit inspection done by next week. This is good to know, so perhaps I should set the HPWC to do 70Amp or less to be on the safe side. Please note my X wont be pulling any more than 48A, so does that alleviate concerns ? I reason I got the HPWC is because it gives me a better, hardwired, relatively more resilient option than UMC+NEMA14-50. Plus the added benefit of pairing it up with another HPWC on the same circuit for the Model 3 next year. I dont plan to have dual chargers on that either, happy with 48A,
Thanks, I understand and agree, it occurred to me while my car(s) may not be a problem, a visiting car may pull more the rated/supported amperage leading to issues. I have also heard that breakers dont trip at the rated amperage but after a tad more tolerance (viz. a 50 Amp breaker would trip at 60Amp) - this sounded nonsensical to me.. curious if that's the case?
Heck even 4AWG THHN at 90° is only good to 95A. The electricians probably just figured "hey, we feed 100A subpanels with this all the time, so we're good, right?"