Thanks! It’s in a wall and the outlet will be within a foot of the breaker. Thanks for the sanity check!As long as you're installing in a wall or planning on running through PVC conduit, this will do just fine. Black/Red for the hot wires coming from the breaker, white for the neutral on the neutral bar in the panel, bare wire goes to the ground bar in the breaker panel.
As long as you're installing in a wall or planning on running through PVC conduit, this will do just fine. Black/Red for the hot wires coming from the breaker, white for the neutral on the neutral bar in the panel, bare wire goes to the ground bar in the breaker panel.
But the necessary factors are all spelled out here; this is definitely fine. It is specifically stated that this is for a 14-50 outlet, and this is 6 gauge copper. That will always cover up to a 50A circuit.It could be, it also could be too small. Wire size for a specific current varies depending on a number of factors
But the necessary factors are all spelled out here; this is definitely fine. It is specifically stated that this is for a 14-50 outlet, and this is 6 gauge copper. That will always cover up to a 50A circuit.
They would not be in the same place. Let's say you are talking about the location that would be "wet". The garage floor has a puddle on it. Well, you aren't allowed to just run Romex cable exposed along the floor that would be wet. Romex would need to be inside a wall, which is not wet, or it can also be inside conduit running along the wall indoors, which is also not considered a wet location.So a garage is considered a wet location for the purposes of requiring a GFCI outlet, but not for the purposes of allowing Romex in it?
They would not be in the same place. Let's say you are talking about the location that would be "wet". The garage floor has a puddle on it. Well, you aren't allowed to just run Romex cable exposed along the floor that would be wet. Romex would need to be inside a wall, which is not wet, or it can also be inside conduit running along the wall indoors, which is also not considered a wet location.
Thanks! It’s in a wall and the outlet will be within a foot of the breaker. Thanks for the sanity check!
Sorry for the thread hijack but I’ve never understood why a high amperage circuit is more dangerous? Similarly I’ve never understood why a 240V circuit is considered more dangerous since it has the same voltage to ground as a 120V circuit.Get an electrician since this is high amp. Just to be safe.
Sorry for the thread hijack but I’ve never understood why a high amperage circuit is more dangerous? Similarly I’ve never understood why a 240V circuit is considered more dangerous since it has the same voltage to ground as a 120V circuit.
If you're pumping enough current through your body to trip a 15A breaker you're already dead. 0.1-0.2 Amps is considered lethal. I don't think the resistance of your body is low enough for the breaker to matter.Current is a measure of voltage over resistance, Ohm's law. It's a high current that burns you and fibrillates your heart. Your body is going to act like a resistor when you join the circuit.
A low amperage circuit is not going to allow you to draw as much current. Given your body stays consistent, a higher voltage is going to draw a higher current, it's a linear relationship.
I’ve never understood why a high amperage circuit is more dangerous
But 1800W is way more than enough to start a fire. Is the probably of a failure that creates a short between 15A and 50A really all that likely? It seems like most shorts would conduct less than 15A (soft short) or way more than 50A (hard short).Thread hijacked. Mission accomplished.
I assume it is more dangerous in the sense that it is possible to generate a lot more heat (I^2*R) in a circuit fault before tripping the breaker? Though I would think 1800W from a 120V 15A circuit would be dangerous enough that even this seems questionable. I could see that maybe with a 50A circuit there might be various catastrophic failures (someone accidentally cuts the line, shorts to something poorly grounded) which are bad enough to immediately cause major problems, but not be enough to trip the breaker. Whereas such major problems would more frequently trip the 15A breaker?
As far as electrocution risk, other than your noted bridging of the hots across your heart, seems no less safe. I thought 240V was strong enough to lock you onto the source, though? While with 120V you just vibrate (that’s what I remember the one time I tried touching 120V to ground...)?
Yes it is.Romex SIMpull AWG 6 CU 3 CDR with AWG 10 Ground TYPE NM-B 600 Volts
That’s on the outer jacket. If anyone can confirm or deny that would help. Thanks in advance!