About a month ago Tesla installed an upgrade to my existing ("legacy") 10-year old 7.92 kW solar system by adding 4.8 kW and 2 Powerwalls.
The ordering and installation went pretty well. It took about 7 submissions to the city to get the plans approved, adding at least 2 weeks to the process, but it finally was approved.
The installers were professional, friendly and very competent. Everyone knew exactly what they were doing and the installation process went smoothly.
After the city approved and the system was commissioned, it looked good at first, but then I started noticing a glitch. From 1 to 4 times every day the Tesla inverter would suddenly stop functioning for about 30 minutes at a time. The result was a sudden drop in total system output during these times, but because the legacy system was still working, solar production did not drop to zero.
Attached is an example one day when the system shut down 4 times.
(I tried to insert an image, but it isn't showing up...?)
The lower red curve shows the power output from the legacy inverter overlaid on the total power output. Notice that during the outages the bottoms of the gaps follow the legacy power curve exactly.
I contacted Tesla using the Chat feature on the support page (which feature works very well, by the way. Each time it only took one or two minutes to get connected with an agent.)
At first upon hearing my description of the outages, the agent tried to insist that I was just seeing clouds and other normal phenomena. I assured her that after 10 years with solar I know what the impact of clouds looks like, and this was not that. After this chat, agents monitored the system and each time they looked it was generating power so they closed the service ticket.
It took a couple more Chats with different agents, and fortunately during one chat the inverter went down and the agent was able to connect to it and see what was happening. This, along with sending in the image shown above, was probably the breakthrough needed, so the technicians could diagnose the problem.
It took a couple more days, and there was even one email from support suggesting that I was causing the problems by "messing with the system" (which I absolutely was not doing), but suddenly one day without warning the dropouts completely disappeared.
In the two weeks since the system has functioned flawlessly, with normal cloud and temperature impact but no inverter failures.
I've heard some horror stories about Tesla taking a long time to respond to service issues, so I'm not going to get too upset about this brief saga. I'm now very satisfied with the system, and love the app that shows so much.
It would have been nice if Tesla had acknowledged that there had been a problem and that they had fixed it, but again I'll live with it.
The ordering and installation went pretty well. It took about 7 submissions to the city to get the plans approved, adding at least 2 weeks to the process, but it finally was approved.
The installers were professional, friendly and very competent. Everyone knew exactly what they were doing and the installation process went smoothly.
After the city approved and the system was commissioned, it looked good at first, but then I started noticing a glitch. From 1 to 4 times every day the Tesla inverter would suddenly stop functioning for about 30 minutes at a time. The result was a sudden drop in total system output during these times, but because the legacy system was still working, solar production did not drop to zero.
Attached is an example one day when the system shut down 4 times.
(I tried to insert an image, but it isn't showing up...?)
The lower red curve shows the power output from the legacy inverter overlaid on the total power output. Notice that during the outages the bottoms of the gaps follow the legacy power curve exactly.
I contacted Tesla using the Chat feature on the support page (which feature works very well, by the way. Each time it only took one or two minutes to get connected with an agent.)
At first upon hearing my description of the outages, the agent tried to insist that I was just seeing clouds and other normal phenomena. I assured her that after 10 years with solar I know what the impact of clouds looks like, and this was not that. After this chat, agents monitored the system and each time they looked it was generating power so they closed the service ticket.
It took a couple more Chats with different agents, and fortunately during one chat the inverter went down and the agent was able to connect to it and see what was happening. This, along with sending in the image shown above, was probably the breakthrough needed, so the technicians could diagnose the problem.
It took a couple more days, and there was even one email from support suggesting that I was causing the problems by "messing with the system" (which I absolutely was not doing), but suddenly one day without warning the dropouts completely disappeared.
In the two weeks since the system has functioned flawlessly, with normal cloud and temperature impact but no inverter failures.
I've heard some horror stories about Tesla taking a long time to respond to service issues, so I'm not going to get too upset about this brief saga. I'm now very satisfied with the system, and love the app that shows so much.
It would have been nice if Tesla had acknowledged that there had been a problem and that they had fixed it, but again I'll live with it.