That's interesting. Going from top to bottom (on either side) the breakers pull power from one leg, then the other leg. That's why 240V breakers come together as a pair. When you snap it in place, once breaker pulls from the left leg and the other from the right so you end up with two legs out of phase with each other with 120V on each leg. If you look at a picture of the inside of a panel with no breakers installed, you can see it.
View attachment 614201
Did you actually watch him connect everything? It could be (probably) just mislabeled. When you trip the one labeled "garage door opener," does it actually shut off the garage door opener?
Edit: I just re-read your original post. Maybe the box in the garage is an odd-ball. But still, killing the garage door opener should confirm.
Can I offer a theory, and its just a theory and I could be completely full of it.
[Completely off base, ignore]
The breakers in the OP's post look to me like thin 1/2 width breakers. Meaning if it was populated with normal breakers the box would have twelve, not twenty four. Someone used slim breakers to double up the number he could fit in the panel. The end result, [/Completely off base
, rambling of someone up to late]
Rest still applies:
which would explain what the op is seeing is instead of every other breaker being on a different phase every two breakers are on the same phase. So positions (1,2),(5,6),(9,10),(13,14),(17,18),(21,22) are on one phase and (3,4),(7,8),(11,12),(15,16), (19,20),(23,24) are on the other phase.. So if he has to use (22,23) or (22,24).
I could be completely off base, feel free to correct me.
24 20a breakers is 480a. I am assuming the OP has only a 200a service. I would love to see the load calculation on that. It might be very easy to overload that box. I can see why the electrician didn't want to put in anything larger than 30a. Might not have wanted to squeeze in even that.
I'll let others comment on other aspects of this. But to me it was a bit dicey even before the extra circuit.