I was planning to use a run of 8/2 MC cable I have to install a TWC.
The 8/2 MC cable is rated at 55a-90degree (or 50a-75degree). Per NEC, 80% derate for continuous load means either 44amps (90degree) or 40amps (75degree).
Since Residential breakers (squareD) are rated at 75degrees I assume 40amps is Max allowable charging on #8thhn (in MC Cable)?
Is it code compliant to use 8/2 MC cable for a Tesla wall charger install with a 50amp breaker at the main and provision the TWC to 40amps max charging?
Is there any eating required for attic install and/or an 80' length of run?