I'm building a house & I had my electrician run a dedicated 100A circuit for my HPWC. In my case, the service entrance & breaker panel is on the side of the house opposite the garage. So the total run of the wiring is probably around 80 feet or so. I know he used copper 3 AWG as called for in the install guide, but for a run that long I'm concerned about voltage drop and heat buildup along the run.
I looked up up the resistance/foot of 3 AWG and came up 0.016 ohms total assuming 80 feet and 0.020 ohms total for 100 feet. So worst case that works out to about a 1.6V drop assuming 100 feet and the HPWC drawing 80A. Doesn't sound bad, but that's still 128W of heat. But then again, given it's a straight run and not coiled up, I guess it's really only 1.28W/ft...
I looked up up the resistance/foot of 3 AWG and came up 0.016 ohms total assuming 80 feet and 0.020 ohms total for 100 feet. So worst case that works out to about a 1.6V drop assuming 100 feet and the HPWC drawing 80A. Doesn't sound bad, but that's still 128W of heat. But then again, given it's a straight run and not coiled up, I guess it's really only 1.28W/ft...