    Quote Originally Posted by JackA View Post
    I would recommend that you consider provisioning a 100 Amp circuit to the new charging location.
    The major difference is that a 50A circuit can be placed on type NM-B 6/3 cable, while 100A requires THHN/THWN #3 in a conduit. The wire cost difference is roughly 2x the cost, but you have to figure in the conduit and installation for that conduit. If it is a short run (40' or so) your materials difference may only be $200. But if you're looking at a long run, you could have a significant expense in the different, and then you'll need to consider whether you'll use the high current or not.

  3. #13
    Member JackA's Avatar
    Join Date
    Jul 2012
    Location
    Orondo, WA
    Posts
    182
    pete8314: I would still check this with a licensed electrician familiar with your local code requirements. My entire materials bill was $453. I had 40 feet of conductor in 1 1/2 conduit, 20 feet of wire from the load center to a junction box where it changed to conduit and conductor plus a new sub-panel and the wire and breaker and connectors. I am not thinking that I would have saved very much by installing a 50 Amp circuit.... again, I am not an electrician.

  4. #14
    MSP P#1117 teslasguy's Avatar
    Join Date
    Jun 2012
    Location
    West Chester, Pa
    Posts
    619
    I also ran a 100amp subpanel to my garage and then a NEMA 14-50 outlet off that. This I can now easily run another outlet for my wife should she also get an EV.


    P1117 Sent from my iPhone using Tapatalk
    PLEASE NOTE: These musings are the copyrighted intellectual property of the author, and are intended as part of a conversation among the Tesla Motors Clubs membership. My words may not be quoted by any third party outside the Tesla Motors Clubs forums, without my expressed consent.

  5. #15
    S VIN S1049, X Resv S744
    Join Date
    Jun 2012
    Location
    near STL
    Posts
    3,307
    Quote Originally Posted by JackA View Post
    pete8314: I would still check this with a licensed electrician familiar with your local code requirements. My entire materials bill was $453. I had 40 feet of conductor in 1 1/2 conduit, 20 feet of wire from the load center to a junction box where it changed to conduit and conductor plus a new sub-panel and the wire and breaker and connectors. I am not thinking that I would have saved very much by installing a 50 Amp circuit.... again, I am not an electrician.
    Your materials bill will be considerably less if you can use NM-B inside a wall. Wire cost is roughly half, plus you save the cost of the conduit. If you can't run inside a wall, Romex must be run inside conduit to protect it, so your only cost difference is the wire cost ($118 for 50' of 6/3 vs. $232 for 200' of #3).

    - - - Updated - - -

    Quote Originally Posted by teslasguy View Post
    I also ran a 100amp subpanel to my garage and then a NEMA 14-50 outlet off that. This I can now easily run another outlet for my wife should she also get an EV.


    P1117 Sent from my iPhone using Tapatalk
    This is a good strategy if you think you'll need an EV at some point. I fed a 125A subpanel from my main panel, and that gives you room for an HPWC @ 80A + a 14-50 @ 40A. But that's because I know I need a high-amp charging solution - the cost differential would be several hundred dollars.

    It's similar to the HPWC vs. 40A charging arguments -- every case is different and if you have the money it doesn't hurt... but for some people it's an extra $300 or so.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Wiring UMC for 110/120 volt operation?
    By smorgasbord in forum Roadster
    Replies: 9
    Last Post: 2012-08-21, 06:51 PM
  2. Mice chewing on car wiring...
    By harry in forum Off Topic
    Replies: 16
    Last Post: 2012-08-21, 02:59 PM
  3. Wiring for Roadster 2.0 Audio System
    By Aspirant in forum Roadster: Technical
    Replies: 3
    Last Post: 2012-03-02, 11:29 PM
  4. Replies: 11
    Last Post: 2012-02-08, 06:21 PM
  5. UMC Wiring
    By W.Petefish in forum Roadster: Technical
    Replies: 92
    Last Post: 2011-09-22, 02:49 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •