Originally Posted by
FlasherZ
Well, we want to be crystal clear here for safety, so I'm happy to clarify. You left me with the impression that you would prefer leaving the ground "unconnected" over tying the neutral and ground together in this statement:
Leaving the "ground" pin unconnected on a NEMA 14-50R is a very, very bad idea, and I don't want to leave anyone with the impression that you should leave it unconnected. That's all. In preference order, 1) you want to run a separate ground from the NEMA 14-50R's safety ground to a safety ground conductor somewhere, so that it's unconnected to the neutral bus; 2) you connect the safety "ground" terminal on the NEMA 14-50R to the "neutral" return terminal on the NEMA 14-50R, then connect that to the NEMA 10-30P's "neutral" pin; 3) you connect the safety "ground" terminal on the NEMA 14-50R to the NEMA 10-30P's "neutral" pin and leave the 14-50R's "neutral" terminal unconnected, making sure there is PERMANENT-QUALITY MARKING that neutral is not present. There isn't a 4th option to leave the ground unconnected, it's a giant safety hazard. For #3, (the suggestion that you not connect the neutral pin on the NEMA 14-50R), see the NEMA 6-20 thread. If your cord is properly marked, it's not so much a big deal but you never want to do this on a permanently installed receptacle (it would unlikely pass inspection).
In *most* cases, the NEMA 10-30R you plug into will be served from a run to the service panel, where neutral and ground are bonded together, and as a result in combination with the fact that the UMC doesn't require neutral, there will be no functional difference between a 10-30R and a 6-30R there.