    Wire Gauge Size for 50 Amps

    Hi,

    After checking out the article here <American wire gauge>, it appears that AWG #6 is sufficient for a 50-amp setup (for NEMA 14-50). However, I recall reading some posts here on TMC saying that it would be better to go bigger (#4, not sure if #5 is common). To my mind, a thicker wire would incur a smaller amount of energy lost to heat (therefore increasing the charging efficiency). Would it be worthwhile to go this route?

    Code:
    AWG#6 - 1.296  mΩ/m
    AWG#5 - 1.028  mΩ/m (21% less than #6)
    AWG#4 - 0.8125 mΩ/m (37% less than #6)
    At 40 A over a wire run of 5 m for 9 hours, total energy lost over the wire run for a 300-mile full charge is:
    for AWG#6: (40 A)^2 x (5 m x 1.296 mΩ/m) x 9 hr = 0.093 kWh
    for AWG#5: (40 A)^2 x (5 m x 1.028 mΩ/m) x 9 hr = 0.074 kWh
    for AWG#4: (40 A)^2 x (5 m x 0.8125 mΩ/m) x 9 hr = 0.059 kWh

    After 300,000 miles, the AWG#4 will have saved around 34 kWh over AWG#6.
    At 0.08 cents/kWh, that's only $2.72, over several years at least.

    So it seems getting a thicker wire will not save money, but it will reduce the temperature of the wire itself during charging.

    I guess my questions are:
    1) How much more expensive is AWG#4 / #5 over AWG#6?
    2) How much cooler will the thicker wire be?

  2. #2
    Senior Member cinergi's Avatar
    Join Date
    Sep 2010
    Location
    Arlington, MA
    Posts
    2,044
    Blog Entries
    1
    Wow, great question and detail there. I don't know the answers (tho pricing should be easy to find online), but one thing came to mind: some 50A device (the circuit breaker or the plug) might not accept the thicker wire -- so just be sure it does if you decide to go thicker.
    SOLD | Roadster 2.5 #1077 | Very Orange | Forged Wheels | Electronics Package
    Model S #SSL146 / VIN #246 | Signature Red | Black Interior with CF Accents | 21" Silver Wheels | Panoramic Sunroof | Performance
    http://fearlessbit.com/

  3. #3
    Model S R77 efusco's Avatar
    Join Date
    Mar 2009
    Location
    Nixa, Missouri, United States
    Posts
    3,020
    Blog Entries
    1
    Here's what my installer used:

    Tesla Charger Installation by efusco, on Flickr
    Evan E. Fusco, MD--Nixa, MO
    Model S R77/VIN-1267-- Black 85kWh (non-perf), Tech, Lacewood trim, tan interior, Sound Studio, Air Suspension, 19" rims, twin chargers, HPWC
    Model X Reservation Sequence # 5966 (for the wife)

  4. #4
    MSP P#1117 teslasguy's Avatar
    Join Date
    Jun 2012
    Location
    West Chester, Pa
    Posts
    653
    Standard for 50amp is 6 gauge for copper. Use #4 for 100 amp. I'm running 100 amp to subpanel on the garage for future addition of another 50 amp outlet for my wife. For me it cost around $200 extra for the #4 vs #6 for about a 40' run. #4 is much thicker wire to run.


    Sent from my iPhone using Tapatalk
    PLEASE NOTE: These musings are the copyrighted intellectual property of the author, and are intended as part of a conversation among the Tesla Motors Clubs membership. My words may not be quoted by any third party outside the Tesla Motors Clubs forums, without my expressed consent.

  5. #5
    Senior Member smorgasbord's Avatar
    Join Date
    Jun 2011
    Location
    SF Bay Area
    Posts
    2,245
    Quote Originally Posted by efusco View Post
    Here's what my installer used:
    Have you had your inspection yet? I don't think 8 gauge wire can be used with a 50 amp breaker.

    The package looks like this: http://www.homedepot.com/buy/southwi...l#.UFENWaTLxZI

  6. #6
    MSP P#1117 teslasguy's Avatar
    Join Date
    Jun 2012
    Location
    West Chester, Pa
    Posts
    653
    Unless using aluminum wire. I think #8 is ok for aluminum for 50amp.


    Sent from my iPhone using Tapatalk
    PLEASE NOTE: These musings are the copyrighted intellectual property of the author, and are intended as part of a conversation among the Tesla Motors Clubs membership. My words may not be quoted by any third party outside the Tesla Motors Clubs forums, without my expressed consent.

  7. #7
    Senior Member
    Join Date
    Jul 2012
    Location
    Randolph, MA
    Posts
    1,689
    8/3 NM-B is rated for up to 45A, since the Tesla mobile connector will be drawing 40A maximum, they can get away with it. Yes, technically it's on a 50A breaker.

    See the chart here: Application Charts

    With that said, I used 6/3 NM-B on my 50A 14-50, I'm also using 3AWG THHN for the 75A OpenEVSE I am building on a 100A breaker, because it was less money than 4AWG (believe it or not, $0.75 per foot for the #3 vs $1.20 for the #4)

    600 Volt THHN


    Mitch

  8. #8
    Member
    Join Date
    Jun 2009
    Location
    San Diego
    Posts
    963
    Quote Originally Posted by teslasguy View Post
    Unless using aluminum wire. I think #8 is ok for aluminum for 50amp.
    Depends on the insulation temperature rating.

    efusco's picture is this product: 125 ft. Black 8-3 Romex NM-B W/G Wire-63949202 at The Home Depot

    If the insulation is rated for 75C, it's good for a 50A circuit. If it's only rated for 60C, it's only good for a 40A circuit.

    Wire ampacity chart: Wire Chart

    The product datasheet indicates that while the insulation is rated for up to 90C temperatures, that comes with the note that ampacities are to be rated at 60C temperatures from NEC.

    http://www.southwire.com/ProductCata...=prodcatsheet6

    So yeah - I'm afraid that efusco's Plug and 100Amp line sticker shock is not yet over - this wire is only good for a 40A circuit which means you can only pull 32A from it with a continuous load like charging your car.

  9. #9
    Senior Member vfx's Avatar
    Join Date
    Aug 2006
    Location
    CA CA
    Posts
    14,794
    A longer run (mine is 180 foot) requires an increased size.

  10. #10
    Model S R77 efusco's Avatar
    Join Date
    Mar 2009
    Location
    Nixa, Missouri, United States
    Posts
    3,020
    Blog Entries
    1
    Quote Originally Posted by drees View Post
    Depends on the insulation temperature rating.

    efusco's picture is this product: 125 ft. Black 8-3 Romex NM-B W/G Wire-63949202 at The Home Depot

    If the insulation is rated for 75C, it's good for a 50A circuit. If it's only rated for 60C, it's only good for a 40A circuit.

    Wire ampacity chart: Wire Chart

    The product datasheet indicates that while the insulation is rated for up to 90C temperatures, that comes with the note that ampacities are to be rated at 60C temperatures from NEC.

    http://www.southwire.com/ProductCata...=prodcatsheet6

    So yeah - I'm afraid that efusco's Plug and 100Amp line sticker shock is not yet over - this wire is only good for a 40A circuit which means you can only pull 32A from it with a continuous load like charging your car.
    Well I don't like to hear that! Let me contact the electrician &amp; see what he says.


    Sent from my iPhone using Tapatalk
    Evan E. Fusco, MD--Nixa, MO
    Model S R77/VIN-1267-- Black 85kWh (non-perf), Tech, Lacewood trim, tan interior, Sound Studio, Air Suspension, 19" rims, twin chargers, HPWC
    Model X Reservation Sequence # 5966 (for the wife)

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Charging Amps per outlet
    By acentre in forum Charging Standards and Infrastructure
    Replies: 13
    Last Post: 2012-12-03, 04:01 PM
  2. How does a battery gauge work???
    By daniel in forum Battery Discussion
    Replies: 10
    Last Post: 2012-09-19, 02:53 PM
  3. Regen Gauge
    By walk_n_wind in forum Roadster
    Replies: 17
    Last Post: 2009-05-08, 11:44 AM
  4. A Better Gauge on Battery Life
    By tonybelding in forum Battery Discussion
    Replies: 2
    Last Post: 2007-09-01, 12:19 PM
  5. GM Hy-Wire
    By AutoExotica in forum Electric Vehicles
    Replies: 3
    Last Post: 2007-03-23, 05:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •